Meron pinapakontrata sakin na electrical plan, bale up and down na bahay. medyo madami ang mga outlets at ilaw nya. Kung susundin ko ang PEC eh aabutin ng 195amps ang main nya. Sobra laki eh. Eto yung electrical draft nya,
Lighting Outlet
Convenience Outlet
Inabot ng 21 branches pwera pa ang main. I'm thinking to sepearte the supply ng ilaw at outlet para lumiit ang main nya. Any comments. Wala rin akong idea kung paano ko sisingilin eh.
BR
Electrical Plan
Offline ahlburuto
  • E&I tech.
Re: Electrical Plan
« Reply #1 on: May 01, 2009, 04:31:44 PM »
Re: Electrical Plan
Offline miGs
Re: Electrical Plan
« Reply #2 on: May 01, 2009, 08:22:38 PM »
BR
What do you mean providing separate supply for lighting and C.O?
D.U will only provide one service drop.
Use derating factors to reduce the load...
Re: Electrical Plan
Offline ahlburuto
  • E&I tech.
Re: Electrical Plan
« Reply #3 on: May 01, 2009, 08:49:28 PM »
As per PEC kasi eh yung mga ilaw eh consider 100watts each yung outlet naman eh 180watts/socket so 360watts. anu bang tamang value na ilagay ko sa computation? As per computation eh inabot ng 60mm2 ang supply cable eh. Pano yung derating factor? Napakalaki nung lumabas sa tawas na size ng service entrance cable at main circuit breaker eh...
br
Re: Electrical Plan
Offline robbietan
  • Pogi/Ganda Points: 17
Re: Electrical Plan
« Reply #4 on: May 01, 2009, 10:08:58 PM »
Lighting Outlet
Convenience Outlet
BR
I would design it as having 2 branches for the lights and the small convenience loads, and a separate branch for each large motor loads. liliit talaga ang main kapag naglagay ka ng service factor sa mga motor loads nya. and I believe only a PEE can sign this plan.
apqi.ph
Re: Electrical Plan
Offline miGs
Re: Electrical Plan
« Reply #5 on: May 02, 2009, 08:32:09 AM »
PEC is using the VA/sq.m method to compute for Gen. Lighting and Outlet, aside from the Small Appliance and Laundry Circuit. All loads must be expressed in VA so that you can compute for the load amperes in a straight forward manner. PEC has a table for the load amperes of motors for their corresponding Hp size. C.O are rated at 180VA (up to three CO in one strap), if these receptacles are not covered by the computation for Gen. Lighting and CO.
From your floor plan, I would have the following circuits:
GF: 1 LO, 2 CO
2F: 1 LO, 1CO
LAUNDRY: 1
SMALL APPLIANCE LOAD: 1
ACU: 3
Check Appendix D3 of PEC for sample computation.
You need a PEE to sign this, so perhaps you can ask the same PEE to guide you about the computation. Every PEE has different approach and style.
PS. I stand corrected about the "derating factor". It should be "demand factor".